Our company in the past has connected the IY4 in a unipolar fashion (signal to In+ and 0V to IN-) and it has worked no problem.

We currently have a system out there that is not working unless we add a 1kohm resistor across the IN+ and IN-. It was working just fine in the shop when we tested it.


According to Rockwell, this specific card cannot work with a unipolar connection.


We thought of putting a signal converter in between but our VAR reported that this will not work either.

Changing the sensor is not an option at this time.

Has anyone had issues with this combination?


Thanks!
 
Just shipped a project with (2) unipolar connections to a IY4, no problems. If it worked fine in your shop and then doesn't at the customer's site, shouldn't you be looking at the installation quality?
 
Thanks for the info.

Per RA tech support:
"It might work a week or a couple of months, put it will fail and possibly destroy the card."

We have a few machines that have been in service for over two years wired this way and have received no reports that there is a problem....

Very confusing.
 
Thanks for the info.

Per RA tech support:
"It might work a week or a couple of months, put it will fail and possibly destroy the card."

We have a few machines that have been in service for over two years wired this way and have received no reports that there is a problem....

Very confusing.
I apologize, I needed more analog inputs so I changed to a 5069-IF8 just before build; I didn't use the IY4.
 

Similar Topics

I am having an issue getting a IY4 to read my thermocouple correctly. We have a R type and K type hooked up and sitting at a known room...
Replies
5
Views
539
Hello Guys, Trying to scale a thermocouple directly into my IY4 card. Connected into the terminal +\-. I’ve scaled the range of my J type to...
Replies
4
Views
1,675
I have a fair amount of Logix and Studio experience, but this is my first project with Studio v33 and a 5069 CPU and -IY4 card. The processor is...
Replies
3
Views
1,151
We switched from a SLC5/04 to a 5069-L320ER, and the SLC's NI4's were replaced with the 5069-IY4, which is a pretty neat card; however, the IY4's...
Replies
3
Views
1,758
Hi folks, I'm doing a valve positioning system (new plc replacing old discrete instrumentation), the old system has position feedback from valves...
Replies
7
Views
2,683
Back
Top Bottom