I apologize in advance for my ignorance.
I am supposed to program a vfd for New Zealand at 50hz.
Any info would be appreciated.
That is the only info I have at this time other that in it is our standard 3 phase 3hp Toshiba drive to run a low pressure pump.

Questions resolve around what I should be concerned w/ changing from 60hz to 50hz
 
Hey Ganut,

Assuming the available voltage is within the acceptable range of the VFD, it should be as easy as entering the motor nameplate data and setting the speed reference to 50hz.


Edit: Obviously the pump will have significantly less flow / pressure too
 
Last edited:
The motor nameplate is the place to start. A lot of motors I see now are rated for 50/60Hz, if that is the case you don't even have to worry about changing to 50Hz. The point of a VSD is that the input frequency doesn't match the output frequency :).
 
like it was said, there is nothing to be concerned about.

in fact, older VFDs that didn't have as much electronics would allow you to take a 3 phase input VFD, and put single phase into it and still be able to run just like normal (at lower capacity of course). nowadays if it doesn't support that, purchasing a single phase input, 3 phase output is very common for places that have industrial equipment, but no rotary phase converter or 3 phase service.

as for HZ. dial in whatever you need for the output, set the maximum frequency to 50hz and it will run fine. If it puts you at ease, i've run into plenty of applications of 60hz systems running 120-140hz motors on them all day long :) read the manual and have at it.
 
We are 400V, 50Hz TN-C here. As long as your drive is rated for that input voltage, shouldn't be an issue.

As others have said, the pump flow will be reduced if originally designed for 60Hz. Suggest finding a suitably rated pump at 50Hz, will be easier for the maintenance guys to replace in future if required.
 

Similar Topics

Hey all, I am currently working on a depalletizer for a customer and we are doing a hoist upgrade. This is a SLC500 processor and the drives are...
Replies
6
Views
297
What would happen if you ran a 60Hz Single Phase Motor on 50Hz supply?
Replies
6
Views
532
the age old question / issue a friend has bought a 1000watt 120vac 60hz rated appliance from the USA into Australia (which has a 240Vac 50Hz...
Replies
10
Views
2,446
I'm located in Australia, my potential client has some equipment recently delivered from USA rated with a 480Vac 60Hz Supply i assume it's 3 Phase...
Replies
14
Views
4,177
Hi I have an IEC motor 4pole motor 50Hz 5.5kw. It is stamped with 1540rpm. Is this even possible for a 4-pole motor?
Replies
13
Views
3,326
Back
Top Bottom