So I am updating our plant 1 line diagrams in Etap and have been doing so for several months now. I somehow always leave the best for last and in this case mean the old stuff.
These old prints are ancient and working with them is making think that I should have majored in paleography as well as engineering.
On prints that show a lot of main feeders and switch gear I see it marked “ Meet 6 Turns of the Hand Requirement” so I am trying to figure out WTH that means? Any ideas?
I asked all the guys that have been here some years and that have been in the trade a long time and no one has a clue.
This almost never happens but google let me down on this one.
Without going into the code very much, you can't have any more than 6 moves of the hand to kill the power to a location or panel (Not sure on that point exactly). But it is refering to and NEC reuirement, try checking a code site. Like http://forums.mikeholt.com/ Have a good day, it Friday.
This sounds like "Article 225 — Outside Branch Circuits and Feeders", ie, Service Equipment. This is not about what are commonly called Sub-Panels or inside branch circuits.
Code:
225.33 Maximum Number of Disconnects
(A) General The disconnecting means for each supply per-
mitted by 225.30 shall consist of not more than six switches
or six circuit breakers mounted in a single enclosure, in a
group of separate enclosures, or in or on a switchboard.
There shall be no more than six disconnects per supply
grouped in any one location.
The above is just some of the code, there are more sections that need to be read and considered.
Remember, the NEC is a minimum set of safety rules, not a design giude. Some plants may implement additional more stringent rules.
The client has an application that when communication between the PLC and the Factory Talk VIEW supervisory fails, the object in the supervisory...
296
I created this FC and it compiles, but when I use it in my MAIN OB1, it appears to have two outputs. See pictures. What am I doing wrong here...
1,484
Hi and Happy new year. I have a GUI done in GT designer 3: on our rig, to turn ON/OFF a motor, it's a 2-step process: Step 1: press the motor...
1,707
The plc runs for a minute and then the power turns off while the supply voltage is OK. I was sure that it was for the power circuit problem inside...
1,990
Hello to all, We have a system where old PLC I/O modules are being used with control logix processor with the help of controlnet adapter module...
2,545