A-B 1747-SN to 5/04 ????
tom_stalcup
Jan 2004
fresno
461
Hmmmmm.... The backround......
I'm planning on setting up some DH+ communications between the main processor of a machine, and the subsection of a machine. Both processors are 5/04's, and the main machine has a 1747-SN card currently being used to feed a remote io rack. The main machines are already part of a network, and the subsections are still stand-alone.
I just wanted to get your take on a few different questions.....
Option 1: Add the secondary processors to the existing network, and add more messaging onto the DH+ network(about 12 items currently on network, this would push it up to 18).(probably what I'll end up doing)
Option 2: Can the secondary processor be hooked up to the scanner card to transfer information that way?(preferred method, if possible)
Option 3: Add some type of adapter to the chassis of the secondary processor so that the scanner card can read information that way?(would take a lot more work/time)
Option 4/5/6/etc..... anything else......
Good Morning Tom,
I think that DH+ is the best way to go. I think you should consolidate your messages though. Even for large projects I rarely have more than one or two message blocks going in each direction.
The 1747-DCM will allow the secondary processor to be viewed by the primary as a remote rack. I haven't used the module in a while and if I remember you can't easily transfer a lot of information with it. You can always mux through it if you want to create a mess.
Good Luck,
(8{)} ( .)
(Yosi)
Stay within the intended service!
If you extend the DH+ you are way better off than the other two options you proposed. The SN module is only to support a RIO network and that only provides you with certain capability. If information handling is your goal, the DH+ is the way to go. RIO is not a great data handling protocol, but then it was not intended to be.
Sorry, I didn't explain quite well enough. There are eight processors and 4 panelviews on the network right now, and the seven slc's are only talking to one slc, with 1 read and 1 write going to each one.(14 messages total, and then the 4 panelviews) Is there a way to consolidate further?
Hi Tom,
Now I see what you mean.
Regardless I'd stick with the DH+ solution. Consolidating further depends on your application. See if you can make use of global data anywhere and possibly eliminate unnecessary messages.
Good Luck,
(8{)} ( .)
(Yosi)
hello I am getting a 57h fault - Specialty I/O module has not responded to a lock shared memory command within the required limit. Fault randomly...
95
We are in the process of upgrading a controls system. The existing system is a SLC500 with some IO cards and a 1747-SDN module communicating to a...
553
se me desprendieron los cables del cable usb quiero soldarlos pero no se como van los cables si alquien me pudiera proporcionar una foto o como...
407
Hello, I've got a project where I need to get information from two ABB ACS880 VFDs onto the plant operator's screen (or alternatively, onto...
23
2,616
Hi Newbie here :yeah: Can one of you experts help me with setting up a simple BTR and BTW to just test 4 analogue inputs 4-20ma (1974-if4i)...