I have some new machinery that I need to tell another machine what speed I am running. The analog output card that I am sending the speed out of is a 1769-OF8C . It is setup with "Scaled for PID" . The analog input card on the machine that wants to know my speed is a 1769-IF8 . It is setup for "Percent Range". would that make a difference ? It seems like they would need to be the same , don't you think ?
The analog output card is coming from, I believe , a PowerFlex 525 Add-On Instruction . The analog output is coming from M1055.Speed_Reference *16383.0 in a CPT , and the Dest is Local:6:O.Ch0Data.
Thanks again ,
I have some new machinery that I need to tell another machine what speed I am running. The analog output card that I am sending the speed out of is a 1769-OF8C . It is setup with "Scaled for PID" . The analog input card on the machine that wants to know my speed is a 1769-IF8 . It is setup for "Percent Range". would that make a difference ? It seems like they would need to be the same , don't you think ?
The analog output card is coming from, I believe , a PowerFlex 525 Add-On Instruction . The analog output is coming from M1055.Speed_Reference *16383.0 in a CPT , and the Dest is Local:6:O.Ch0Data.