AB ControlLogix 5000 Ethernet EWEB Scan Time
devker
Apr 2007
Pohang
Hi,All
I can't express my opinion well in English.
You can't understanding, I am very worried about my write.
I'm communtcation between AB EWEB module ControlLogix 5000 and VME using socket programming Ethernet.
We were proposed 460byte data size every 25ms send and received.
VME to PLC successful.
but,PLC to VME failed.
PLC side configuration two Task scan.
one - Continuous - normal program
two - Period(25ms) - PLC<->VME Communication program.
PLC write MSG
writeMSG.EN
----|/|-------------------------------- writeMSG ----------------
but, This MSG not execute every 25ms. The same TON Timer.
reality check time execute 50ms.
socketWriteTimer.DN
----|/|----------------------------------- socketWriteTimer -----
Preset 25
Accum
socketWriteTimer.DN
----| |----------------------------------- writeMSG -------------
I'm guess scan time timing AB PLC SOTS(System Overhead Time Slice 10%) and writeMSG.EN reset or socketWriteTimer.DN.
I'm propose every 25ms data send.
Will you give me some advice?
EWEB should be able to do it, I tested it while ago with 5ms task the allows it send MSG every 10ms
Just remember that any message takes two scans to execute: Message needs to see both OFF-ON and ON-OFF rung conditions to restart
So change periodic task to 12.5ms and you should be able to send it every 25 ms.
Just want to make sure you understand:
- DN bit on the Write message indicated that EWEB put data on the wire and not a delivery.
- It may take more than one scan for EWEB to complete message so may not get your 25 ms all the time.
- Message processing at 12.5ms may put heavy loat on you processor leaving little time to execute cont task and comms.
- In any case you should have SOTS at least 20% may be more
Thank you very much.
I can't begin to tell you how grateful I am.
Yor are an expert in the field.
Hello, I’m communicating a ControlLogix 5000 with a Yaskawa A1000 drive, via a Ethernet 1756en2tr module. I installed the drive interface as a...
3,096
I have an older PB32 app on a PV600 that was talking DH+ to a PLC5. Well we dumped the PLC5 for a CLX and the plant exchanged the PV600 for a...
4,053
I have a Controllogix5000 system that I am retrofitting a quantity of 4, Powerflex 40P Frequency Drives onto the system. Two of these drives have...
1,975
Has anybody been able to control a CV5000 vision system using commands via ethernet/ip with explicit message instructions, or by any other mean...
4,530
We have an Allen Bradley ControlLogix 5000 system operating for about eight months. It controls a stamping machine. anyway, it broke down on...
18
21,966