AB flex I/O problem

m_prantik

Member
Join Date
Aug 2011
Location
kolkata
Posts
1
hi friends

I have a problem with flex I/O node connected with ab plc 5/40C series through R-I/O network. PLC is not reading that particular node(node 05). all inputs are aero , outputs are one though inputs available from field.
what we have tried:

changed i/o adaptor module.
swapped i/p, o/p card & i/o adaptor with other node ....... those are working fine there.
configuring node 05 with new address node 07, 08 etc. no result.
connected node 05 R-I/O network with node 06 and vise versa.... no result.
plc i/o config also showing node 05..... no fault indication any where.

Please help me.

IS THERE ANY RUN OR ACTIVE BIT TO BE SET FOR FLEX I/O IN R-I/O NETWORK.

PLEASE HELP ME.........

P.K.Mondal
 
1.Terminal resistance--have u checked?
2."connected node 05 R-I/O network with node 06 and vise versa.... no result."-not clear..
r u connection original node # 6 in Node #5 ? and then also node # 6 running ok & node # 5 not detecting?
3. there is some "enable/disable" function in processor properties...u have to check/uncheck...
 
1) Check the wiring polarity on the blue hose.
2) What is the configuration of the port in the PLC (ie. baud rate)
3) Post the DIP switch positions for the node so we can determine what you need.

Good luck,

(8{)} :) .)
 
Make sure if you are using a 32 input module that your ASB module is revision E or higher, lower revisions will not work with the 32 input module.
 

Similar Topics

Hello Friends I have a project with 3 Powerflex 525 EENET. When I try to open the Drive properties the next message appears: Host revision 6.1...
Replies
2
Views
2,543
Greetings all. First post here, new to RL, MODBUS, pretty much all things PLC, so please forgive me if I'm asking dumb questions. - I need to...
Replies
11
Views
6,178
I recently swapped out a powerflex 755 that failed in service with a new one. However when installing the HIM module back into the new drive, I...
Replies
8
Views
3,876
I have an application using a Powerflex 525 for positioning. I really should be using a servo but the equipment is already in place. I have...
Replies
4
Views
2,049
I have a system that has about 40 PowerFlex 525 VFD's on it. They are all running conveyor belts, not a difficult application. Most are 1HP...
Replies
6
Views
3,453
Back
Top Bottom