AB ML1500 to Emerson servo over ModBus
Allan Barnes
May 2004
Woodstock ON
122
Has any one run into a problem where the Most significant and least signigicant words between 2 devices are different.
This seems to be my problem when writting a Long Int from the ML1500 to the Emerson Ei-203.
In my ML1500 I use a "CPW" to move my data from Longs into Intagers, swap the MS wors with the LS word, then send them off to the servo.
For my feedback from the servo I do the same but in the reverse direction.
This works great untill I have Negative Number, then the Index Distance I have sent my servo goes all waky, and the servo makes a very long index.
Note: the data type in the servo is definetly a Signed 32bit integer
Any help would be greatly appreciated.
Ok so I dug a little deeper.
Turnes out when I use the CPW function to turn the 1 long integer word into 2 integers, the CPW only writes to the first integer and not the second integer.
So because the Second words is All 0 at the bit level my servo distance is all wonky.
SO how do I move the Long into 2 ints and keep all the bits in both the MS Word and the LS word.
Going from 2 ints to 1 long seems to work flawlessly (hopefully by saying that I do not activate a curse)
Hi all, PLC : Micrologix 1500 lrp HMI : Renu FP3070 TN I am a beginner in the plc world. I am trying to connect the renu hmi with ML1500 lrp in...
766
Hello folks, Hope everyone is doing well. I am a beginner at working in analog signals with PLC Analog module: 1769-IF4 ( 4 analog inputs ) PLC...
1,356
I have a Allen Bradely 1500 that has a cracked board. It still works but needs replaced (battery is no longer connected). To make migration easier...
3,225
I inherited a system with the Micrologix 1500 talking to 8 VFDs using Modbus RTU protocol. One of the VFDs was replaced with a Toshiba VF AS1...
1,205
Hello, I have the PLX setup and configured. Its seen and downloaded to. However my ML1500 does not communicate over it. The port (0) is used...
1,653