ab problem

gary marano

Member
Join Date
Mar 2005
Posts
16
I am trying to connect to a rs logic 1000 plc and i have slc500
software on my lap top i hope i said that right. What my problem
is that i get a window saying driver not configured. But yet
on the upper left hand below the no edits their a driver number.
rslynx is installed i do not know how to configure a driver to
my laptop. I also get a no response from processor at selected
path/node. What the hell is a node? Yes i am a newbe please help!
At the top of the screen their is a window saying driver but when i click on it all it says is driver.
 
Try this.


Go to RSLinx and get to the "Configure Drives". It is the middle icon that looks like a cable. Click on the drop down field for available driver types. Then highlight RS232 - DF1 and click on "Add New". Click OK for the default name. Another menu box opens up.

Click in the Device Drop dwon box and select SLC CH0/Micro/Panelview. Make sure you are tied to the MicroLogix 1000 then hit Auto-Configure. This should set you up automatically.

Good Luck,

Todd.
 

Similar Topics

Hello, I need to write the following program in Ladder language, but I could not integrate the Fibonacci sequence into the ladder. Can you help...
Replies
11
Views
169
On all pages of my project i have a lot of information, texts and details that should not not be shown. I can remove them for each part apart from...
Replies
0
Views
41
Hi, I have had problem with upgrading some projects from v16 to v18. I tried it on 3 diffrent computers. I want to post this so that anyone that...
Replies
3
Views
183
Hi, I am having a challenge installing a new drive ACS355-03E-44A0-4 as it keeps on displaying Fault code F00018 even when the load is not...
Replies
3
Views
135
I have an issue on my vessel, we have water tight door system created in China, company is no longer operating. We have 7 doors each with their...
Replies
4
Views
147
Back
Top Bottom