AB servo drive fault
Mtech
Mar 2010
Indiana
132
Need help finding a servo drive module fault code,16#0800_0000. Tried fault help but it only shows one code of 16#0810_0000. I got the equipment back up and operating but would like to find a discription to this alarm. Thanks in advance.
Module type:2098-DSD-010-SE
Motor type:MPL-A320P-M
http://literature.rockwellautomation.com/idc/groups/literature/documents/in/2098-in003_-en-p.pdf
In section 4 of the manual you will find any fault code that deals with Ultra 3000 servo.
I see this fault at times. It is a software overtravel fault.
Should be some type of over travel limit switch or prox swith on your machine that would keep this fault from happening. If the trigger tab does not actuate the switch then the program will stop the servo because of an overtravel condition.
I hope this helps.
Thanks for the reply. I will research program file for programmable limits as there are no hardware devices to detect. Its been awhile but think there is a software limit setting in properties. I will dig into thank you
I am new to programming rockwell and could use some help. I am using compact logix controller with an Ethernet IP Servo Drive. The servo has 400+...
3,211
All the servo guys out there looking for a little help? I am having issues with a Kinetix 5500 keeps giving me S39 BUS POWER LEAKAGE FAULT. Does...
1,968
I kept getting Kinetix 6000 servo drive fault of E04 (motor overtemp fault). The servo motor is MPL-B450F. The motor was barely warm, certainly...
9,665
Friday, 01/03/2014, at the end of the work shift, I was made aware that an Allen Bradley Ultra 3000 Digital Servo Drive faults occasionally with...
24
22,575
Have an Elwood SX servo motor and a IndraDrive (Bosch) amplifier controlled by IndraControl MLC (i.e. PLC). Upon connection, message referencing a...
3,951