about slc5/03 and the 1747uic
I had problems with this device in the past. If someone plugs an ethernet cable into the RJ45 connector on the front, the device no longer functions properly.
Open the program and on the project tree click communication, then you will setup the port.... I don't have RSLogix on the PC but will post a screen shot later if someone does not do it before
Do you have a copy of the program? if you post it we can look at how its setup
see attached, the first is the default setting, second is how to set the DB9 port to DH485
Well, I commented that I could connect to the PLC through the RS232 port SLC5/03 plc. as you said the port was configured for DF1 and I had to set to DH485. (y)
Glad you got it.... but it was Mickey in post 3 (two days ago) that said you need to configure the port to DH485 (y)
I have wasted a week trying to figure out how to connect an SLC5/03 with my laptop. I do not have and can not Buy the 1747 UIC and PC3 cables. I...
2,578
I am trying to connect to SLC5/03 using an FTDI usb to rs232 with female to female converter at 1 end... however I can not connect to it ... the...
1,294
Good evening. I am in serious need of help. I am trying to connect a Panelview Plus 7 Standard to a SLC5/03(1741-L531) using a Moxa MGate...
653
Hi. I am having trouble establishing comms between an slc5/04 and panel view plus 7 via a PLX51-net-eni. The set up is: 5/04 Channel 0 DF1...
942
Hi All, I have programmed some MSG instruction in SLC5/05 64k CPU series D FW 13 brand new cpu. 2 of the MSG instructions are direct IP to other...
991