AC Current into an analog input card?
hd_coop
Jul 2002
Belgium, WI
319
Hi all,
I am working on a machine right now which is spinning a flywheel past a sensor. The sensor is creating an AC voltage everytime a tooth goes by. This voltage is about 400 mV max at the speed we are running the flywheel at. We have this going into an AB 1746-NIO4V analog card. We are getting a usable signal right now which works well.
My question is if there will be any adverse effects of sending AC into a DC analog card? Will the life of the card be reduced? The frequency of the wave is 30 Hz
Thanks for your help
The Input Specification for this module in Voltage Mode is -10 to +10 VDC. As long as the peak AC voltage does not exceed 10 volts, you won't damage the module. I can not say how the module will respond to the AC voltage.
you may get a more stable reading if you put a rectifying diode and smoothing capacitor in circuit.
If you can envision a sine wave, 30 times per second it is rising from 0V, to a peak voltage determined by your alternator, back down to zero, down to the negative of your peak, back up to zero. e.g. 0V -> 400mV -> 0V -> -400mV -> 0V.
Depending on when in this cycle your input card makes its sample, your voltage reading will change.
I am actually surprised that you do get a useful reading from it, as is.
Check out this result from my quick google search on half-wave rectifiers...
http://engineering.dartmouth.edu/other/3Dcircuits/animations/rectc.html
Hello My analog sensor outputs 4-20mA only. My analog PLC input sees 0-10V only. How can I make this work? I tested out a different sensor...
1,802
I've got this 1756-IF8 card configured for 8 single ended inputs as shown below, but none of the channels are read real values (about 4 ma in the...
2,570
hi . we are using beckhoff decentralised I/O module on profibus , which has its different analog cards for RTD , current and Voltage input. i need...
5,911
In my 1746-NIO41 analog input card , for a full 20mA input , the reading shows only 16383 ,why is it so ? for input address "i:3.1"
1,991
Hello, I have 4-20mA 2-wire transducers powered using external power supply (passive analog module inputs). How can I protect PLC inputs from...
8,728