https://www.youtube.com/watch?v=jg1mYsIrFPs&t=65s
Since the values 3.4, 3.8, and 4.2 cannot be
exactly represented in IEEE-754, or any, floating-point binary (base 2) format, when converting to decimal symbols ("1.234567890..."), at some point the symbols
must diverge from the rational number (34/10).
When adding two such numbers together (3.4 and 0.4), the combined "error" will show up in the least-significant digits.
- 3.4
- may display as 3.4,
- but it is internally 3.400000095367431640625000000
- I don't know why it does not display as 3.4000001
- 0.4
- may display as 0.4,
- but it is internally 0.400000005960464477539062500
- The sum of those two internal values is 3.80000019073486328125000000000000000
- which will display as 3.8000002
Logix REAL format representation is 32-bit: 1 bit for sign; 8 bits for exponent; 24 bits for mantissa. The mantissa represents a number in the range [1:0b10) i.e. in the range [1:2) N.B. the right side is exclusive. In binary:
0b1*0000000000000000000000 <= equal to 1
0b1*1111111111111111111111 <= slightly less than 2
Where
- 0b => prefix indicating the following symbol is a number in binary, that is, the only available digits are 0 and 1
- * => a "binal" point i.e. a binary analog to a decimal point,
- so,
- in decimal i.e. base 10: (15 ÷ 10) = 1.5
- in binary i.e. base 2: (0b11 ÷ 0b10) = 0b1*1
- N.B.
- 0b11 = 3 (decimal)
- 0b10 = 2 (decimal)
- (0b11 ÷ 0b10) = (3 ÷ 2) = 1.5 decimal = 0b1*1 binary
So, 0b1*11111111111111111111111 = (0b111111111111111111111111 ÷ 0b100000000000000000000000) = (16777215 ÷ 8388608) decimal = (2 - (1 ÷ 8388608)) decimal
The exponent part of the IEEE-754 moves that binal point to the left or the right, the same way the exponent in the scientific notation representation 1.50000e3 (1.5 x 10
3) moves it to be the equivalent 1500.00 in non-exponential decimal symbol format.
And finally: the magnitude of the right-most bit is between one-8388608th and one-16777216th relative to the value itself. i.e. around one part in ten million i.e. 1 part in 10
7. So any error between the rational number expressed in the IEEE-754 binary number (0b1... ÷ 2
exponent) and its decimal representation will show up around the seventh significant decimal digit to the right of the most significant decimal digit.
Caveats
- I chose * instead of . for the "binal" point so the two would not be confused here
- The term "binal" point is not a real word; I just use it because calling the delimiter between digit places representing values greater than or equal to 1 (1, 2, 4, 8, 16, ...) from those less than 1 (0.5, 0.25, 0.125, 0.0625, ...) a decimal point might be confusing