The new button has been added and logic is all set for it. It is conveyor on/ off button and working properly but I was not able to make it display an alarm when it is switched off. How you make an alarm display on hmi ? Is it using a Factory talk view or RSlogix 5000 software? Thank you, Ziya
I could reply with "There are hundreds of ways, which one do you want to use?". The question is a little vague and smells like homework (maybe it's not, but maybe it is?). Some clarification if you could? You say "I was not able to make it display an alarm when it is switched off". Show us what you have so far.
I have attached a file and I want hmi to display that message when toggle switch is OFF position.
You need to use FTView Studio ME (Machine Edition), and go into the left tree of your project.
Do you have RSLinx Enterprise Configured to point a Short Cut to the PLC?
If not, you should do that first.
To configure a short cut, you need to look as some YouTube Videos if you do not know how to do this.
This also explains the process...
http://bryceautomation.com/index.php/2017/09/13/factorytalk-view-project/
Getting back to Alarm Configuration
Open the Folder "Alarms"
Double Click "Alarm Setup"
Click "Add Trigger"
If you are going direct to the PLC (which I recommend), you can browse to the tag (If you have offline project defined, or you are online with Processor), or you can just type it in in the following format.
{[PLC]PUMP_STOPPED}
After you have your trigger defined, now you have to assign the trigger to your alarm message, on the second tab "Messages".
You will need to add an object to your project to display the alarm "Alarm List" Object.
There is a bit of configuration (check boxes and pull-downs) but it is self explanatory.
The following steps are taken.
Open factory talk view studio
Locate alarms folder and click alarm setup.
Go to message triggers on the pop-up screen. Add a new message.
Then go to the applications tab scroll down to create runtime application and follow through the step.
The last step is to click transfer utility under tools and download them back to HMI. Thank you, everyone.
Hmmm... The Auto Discovery was working well until I got to the last two cards. Then I got this: "device cannot be added because there is no room...
762
Hey there, I have a SLC5/05 in a 13 slot rack with a 1747-SN RIO Scanner. The scanner is connected to a PLC5 remote rack. I have to put a...
1,746
Sorry for these basic questions. Eventually I'll surprise you with more sophisticated stuff. I just added some new tags in this PLC app. And...
3,135
Dear experts, I need your advice. I am working on project where we use S5 135U system. Our configuration: CPU: 6ES5 928-3UA12...
1,780
Would someone be able to tell me how many Input/Output cards are allowed after a CompactLogix L30ER and a 1769-PA2 power supply. At the present...
5,508