S5 135U, problem with added 32DO card

LuboV

Member
Join Date
Jun 2015
Location
Slovakia
Posts
8
Dear experts,
I need your advice. I am working on project where we use S5 135U system.
Our configuration:
CPU: 6ES5 928-3UA12,
MOBY:6GT2002-0AA00,
6x32DI cards,
2x32DO cards.
Rack has 21 slots.
I need expand digital outputs with 32DO card.
When I add new 32DO card, I can not switch on any output(on added 32DO card).
Card is OK..I tested it.
Where is the problem?
 
Last edited:
Hi Manglemender,
thanks for your advice.
I read about it in manual, but I do not have DB1 in plc.
DB1 is used in multiprocessor operation.
 
Did you set the right address?
The switches are on the upper left side of the card, if I remember correctly. You must add 4 to the former highest output card address.

And you must connect the power supply and the enable -pins of the front connector.

Kalle
 
Last edited:
The address is set correctly. First DO card has address 20, 2nd.card->24, new one->28).
The output card (6ES5 441-4UA11) is connected to power supply -> pins:1 and 3.
I dont know what is wrong :(

Lubo
 
The address is set correctly. First DO card has address 20, 2nd.card->24, new one->28).
The output card (6ES5 441-4UA11) is connected to power supply -> pins:1 and 3.
I dont know what is wrong :(

Lubo

I think you need a cold start after you insert the card.

If you, from the program, try to write to the Q 28++ outputs; does the ADF LED lighten?

Kalle
 

Similar Topics

Good morning Please i need an advise, I have a s5 135u cpu system , it is installed on printing machine. Nowadays its stop about 10 times in 8...
Replies
27
Views
4,266
hi... i'm newbiew about this hmi and plcs... And... there is this old application running on ancient "windows 3.1". i think it's communicating...
Replies
0
Views
1,357
Hi, I tried to backup program from PLC but all I got was couple of DB's and DX's. I used STEP5 and S5 for Windows, both showed the same blocks...
Replies
5
Views
1,965
problem in a communication that lost bet. S5 135U (ALARM S3964RDDE SERVER) & In Touch Hi all experts and members ...
Replies
0
Views
2,126
Hi All, My company recently bought a used press with a S5-135U plc with a 921 CPU. This machine has not run in over 3 years. We are trying to work...
Replies
7
Views
2,086
Back
Top Bottom