Good afternoon all,

I have an AB SLC 5/03 which uses multiple AC i/o cards (such as 1746-IA16 and 1746-OA16). I am using a 7-slot chassis with the first being processor, and next 4 being i/o cards. I am looking to install a 1746-IB16 (DC input card).

Question: Does the 24V supply for the input card have to come from the same 120V power supply that powers the rest of the PLC or is it acceptable to grab 24V from a different 120V power supply that does not touch the PLC at all?

Thanks,
 
The I/O is electrically isolated from the PLC's logic power input (very much intentionally !).

Your 24V inputs just have to be relative to the DC Common you connect to this specific input module.
 
For sure, for sure, thanks for the reminder.

So if you plug in a module with the power on, it will fry it? Sometimes we have I/O cards that become loose from the back-plane, but our techs just push it in, even with power on. I'm unsure why it would've fried your Power supply, especially if the slot is disabled in the program?
 

Similar Topics

Hi, I've run out of analogue input channels on my Q68AD-G module. If I add a new Q68AD-G module and install it into a spare (blanked-off) slot, it...
Replies
2
Views
1,340
I have never understood how the I/O is configured using RIO. In the tree there is only the RIO module, not the racks of I/O attached or all the...
Replies
2
Views
1,300
I need to add a QX10 module to our PLC because we've run out of DI channels. Does this module need to be configured in a similar way to the...
Replies
7
Views
2,220
Hi, I'm planning to install a new Analogue Input module Q68AD-G. It will inserted on Rack 0 Slot 4. When it's installed, will the code recognise...
Replies
6
Views
2,434
Good Evening , I'm getting ready to add a few input and output modules to a 1769-L33 rack. The module's I'm going to add are 1769-IR6 ...
Replies
0
Views
1,648
Back
Top Bottom