Air/Fuel ratio by controlling flow rates
ddeshi2
Dec 2010
Baton Rouge
89
Hi all, I'm new to PLC Programming and this is my first project. In our project water, air and natural gas are fed to a combustion chamber and the mixture is ignited. We feed water first, then air,then natural gas. I have to control the flow rates of all the three and also the air/fuel ratio. How can I control the air/fuel ratio by controlling their flow rates? For example, Air/fuel should be in the ratio of 10 to 1 ..can I achieve it by using single PID loop.. CV of Air becomes the set point of Natural gas and the valve is opened accordingly? Am I right? Please Help..
Thank you,
Ding.
What you have described doesn't sound like a single PID loop to me. It sounds you want to use the output of the air PID loop as the setpoint for the gas PID loop. Why do you think this will give you better results than making the setpoint of the gas loop one tenth the setpoint of the air loop?
>We feed water first, then air, then natural gas.
The English meaning is a sequence of actions: water, then air, then fuel. If that's actually the case, ratio won't work because only one oomponent is being added at a time.
But doing so creates a chamber full of fuel and air, essentially a bomb (an explosive mixture), not continuous combustion.
What's really going on here?
Hello! I am upgrading a furnace control system that will be using natural gas and combustion air ratio control. This will be done on a plc5/20e...
7,998
I am about to be upgrading several compressor engines to Logix 5000 and I am looking for the best, proven, ways to program in the various curves...
2,071
Hi, I have looked at the other combustion threads and have a few questions relating to my own system. I have an in place system (predating my...
2,075
Hello All, I've been tasked with automating a flatbed press that runs with some pretty extreme temperatures. I've been told it can run close to...
189
418