Hi, I'm using an Allen Bradley 1769-IF4 Analog input crd with a Compact Logix L33ER. Its 14 bit (0-16384), and I'm taking raw readings. I am applying and measuring (with a multi-meter) a precise voltage of 1.50 volts across the analog input terminals. I'm configured for a single ended input signal, 0 to 10V.
The input value I am getting is 2350 which equals 10* 2350/16384 = 1.43 Volts.
The card specs say that it is internally calibrated yet this error is approximately 4.7%, way outside the specs for the card (0.2%). I am not observing any steady state offset or noise on the signal.
I know I can apply a fudge calibration factor in PLC code, but am curious if anyone else has used this card and achieved better accuracy, and what procedure they were using.
Thank you