Hi Guys
Slightly off topic sorry , but you guys know everything :)
And I need your advice
You can run this type of inverter as I understand it , the "proper " way
And have it powered up , then give it a run signal
OR
Have the inverter in line and be powered up in the circuit when the contactor is energised
My question is this :
If the inverter is only powered up AFTER the contactor is energised and it goes through its power up routine it does not see the run signal ( term 2 and 11 shorted )
However , if I break and re make the run signal after power up , it runs up to speed
Any help and advice appreciated
Refer to parameter A543 'Start At Powerup'
Its default is 0 - requires transition after power up
Change it to 1 to allow your situation.
Note: this may have safety implications. Please consider you installation carefully.
The manual has further information
That's great ,
I had explored the basic parameters
But obviously missed the more specific ones
D'oh !
That's very helpful , thanks
Got this new to me powered on today and have no main air and the only problem I have found is the f059 on the vfd. S1 has 24v, none on S2, and 48v...
481
hi, I have a PLC that has been running for a few years now, and recently the SMTP was moved to a different server and IP address. we noticed...
3,071
Just had an interesting dilemma. 6 powerflex 525’s changed their max hertz on 5 different machines all are connected via Ethernet but do not work...
2,535
we have a 525 drive with a 25-comm-f2p module. that was giving us 4 solid red light for communication. replaced module now we get port light is...
1,348
I have a question about a couple of parameters on the 525 Drive. The parameters are as follows: P033 Motor OL Current P034 Motor NP FLA What...
4,462