allen bradley 525 vfd
jimcav
Dec 2004
new jersey
229
Ok I will do my best here I have 16 525 vfds all connected via ethernet to a net gear managed switch I have the IGMP snooping turned on. When the system is turned on in about 5 min the I will get a F073 enthernet comm alarm. Any clue??????
Using compact logic 1769-l33r
Jim Cav
Do the switch management features show you any hardware problems on any of the ports ? What about the diagnostic web pages of the drives and the controller ?
Are you using unicast or multicast connections to the drives ? The IGMP Snooping feature only applies if you are using multicast.
Do ALL the drives give you errors at the same time, or just specific drives ?
Do you have the latest firmware in the 525? I heard a rumor from a local Rockwell contact that there is a known issue that was not repaired until the latest firmware release that causes unexplained timeouts on Ethernet.
In the process of upgrading the the firmware I will keep you posted.
Thanks for all the help.
FYI:
We tried flashing 525 firmware with a USB connection and tanked both times - both drives were left in a state that we couldn't flash again (at least with USB).
We finally flashed with ethernet and had no problems. We were also able to recover the 2 previous drives using the ethernet flash.
Got this new to me powered on today and have no main air and the only problem I have found is the f059 on the vfd. S1 has 24v, none on S2, and 48v...
537
hi, I have a PLC that has been running for a few years now, and recently the SMTP was moved to a different server and IP address. we noticed...
3,109
Just had an interesting dilemma. 6 powerflex 525’s changed their max hertz on 5 different machines all are connected via Ethernet but do not work...
2,563
we have a 525 drive with a 25-comm-f2p module. that was giving us 4 solid red light for communication. replaced module now we get port light is...
1,364
I have a question about a couple of parameters on the 525 Drive. The parameters are as follows: P033 Motor OL Current P034 Motor NP FLA What...
4,567