Allen Bradley Compact Logix need help

THank you guys,

I ordered the end cap few days ago and
I received the 1769-ECR yesterday.
I put the end cap on the PLC and I try to run my program, but I have always the same error....

(Type 03) I/O Fault (Code 23) “At least one required connection was not established before going into Run mode."

Moreover On the modules, the error says :

(Code16#0203) Connection timed out

I didn't change my program, what do I do ?

Thank you very much
 
Last edited:
If "test_with_manual" .zip within post #9 is still your current project file and the current hardware configuration is the one from the pic in the same post, then you have two modules unaccounted for within the RSL5K project you are downloading to the controller.
Slot1 contains an Analog Module which is not in the project tree and Slot4 has a Communications Module also inexistent within your application file.
As a rule of thumb, within any RSL5K project Rev.19 or lower, any module installed in the physical rack has to be included into the application file's project tree prior to downloading it to the CPU.

The faults you are experiencing are caused by the CPU's "lack of knowledge" about the devices which are trying to establish communications.

In the Offline RSL5K file ADD the two "extra" devices to the corresponding slots and then download again; use SAVE after every Offline/Online hardware/program edit.
 
Last edited:

Similar Topics

I was wanting to see if anyone had any information on setting up a cub5 meter and getting the data to a Allen bradley PLC. I think i have the set...
Replies
0
Views
135
We have an AB PLC that has a faulty expansion cable between Bank 1 and Bank 2. Part # 1769-CRR3. I found a small burn mark on the board. Being...
Replies
1
Views
760
Hello everyone I have an Allen Bradley Compact Logix 1769-L18ER-BB1B. I have several processes that I would like to start based on time of day...
Replies
9
Views
2,670
I have two L35e processors i want to send message to and from. I just want to do data read. Condition from one plc and see it on another plc. I...
Replies
5
Views
2,219
Above mentioned HMI is installed in my plant with Micrologix PLC. Yesterday the HMI suddenly stopped working during plant operation and HMI's...
Replies
3
Views
4,930
Back
Top Bottom