Allen Bradley power consumption calculation
elmatador
May 2008
Canada
108
Hi Guys,
I have a project with 10 Controllogix racks. I need to calculate power consumption.
For example, say if i have 16 analog input channels, would the following be correct?:
16channels*24VDC*20ma?
What would I do for a Discrete input and Discrete output cards and Analog output cards? I will need to take into account the worst case current.
Does the Rockwell Architecture builder actually take this into account or does it just calculate RACK POWER consumption and not the consumption of analog transmitters, control valves etc.?
I basically need to compute the power rating of the main 24VDC power supply going to the racks and instruments.
Out of 10 racks, that is all you have? Your calculation is going to be based on the type of I/O your using. If you are just concerned with the consumption of the CLX power supplies then you should be able to collect that data from the AB website in the manual.
There are many variables that are in question.
use the max calculation as you are doing and then multiply by two for the maximum power rating as the temp has influence.
We've still got a ton a PLC 5's installed and running. We lost a 1771-P7 Series B power supply. There are a lot of 1771-P7 series D power...
245
Hi everyone. I have an issue with an Allen Bradley PLC model 1769-L30ER. This PLC had a previous program with a different IP address but when I...
541
I have several 5069-AENTR adapters in a system. All of the IO is 24VDC. Can I use the same power supply (24VDC) for both SA and MOD power into...
551
Have some equipment that have the micrologix 1400 1766-L32BWA. all of our equipment in the locations have 208-220vac 60 hz power. Was just told we...
1,754
Hi All, I'm having some trouble on determining the total power consumption of the following I/O modules: 1769-OB32,1769-OF8V, 1769- OW16...
2,649