Allen bradley Powerflex 700 fault light
eebads2391
May 2008
Stockport
112
Hi ,
I have an Allen Bradley Powerflex 700 Inverter
It has a green power light ( led ) and under that has a status
Light ( led )
The Status ( sts ) light is a steady yellow whilst the drive is running
The manual indicates Paramater 211
I have checked this parameter and it shows
000 000 000 x 000 000
Does x indicate the fault ?
Many thanks in advance
Mike
No, that bit is reserved or not being used.
The zeroed bits indicate that none of those alarms is present.
I recommend to check parameters 211 and 212. When you find a bit set to “1” in 211 or 212, go check in the user manual what alarm that bit corresponds to.
Bye
Jose
Thanks Jose, I will check further
None of the bits are 1
It looks like the fault isnt showing
I will check parameter 212
Many thanks
Got this new to me powered on today and have no main air and the only problem I have found is the f059 on the vfd. S1 has 24v, none on S2, and 48v...
476
Greetings everyone, I know there is a way to programmatically set the date/time on a 750 series VFD (look up Rockwell automation sample code)...
1,049
Can someone do me a huge favor and print these 2 Allen Bradley DNO files and email them to me? [email protected]...
1,760
Hi all, Client with a pretty much brand new AB Powerflex VFD starting throwing Fault 17: Input Phase Loss this afternoon. Started doing some...
9,506
We have a Powerflex 753 drive on a 192.168.1.X network that I can communicate with a Controllogix L71 with no issues on same network...
1,436