I am guessing that your existing system architecture is several F-P single loop controllers tied with a serial communications link to SCADA software running on a PC. The PC based SCADA software is probably what I call a "leg saver" system. Instead of having to run around the plant with a clipboard to log operating data, and having to acknowledge alarms and tune the controls at each individual station, the operator can do these functions at the PC.
You can provide the equivalent local control using a micro-PLC at the location of each F-P controller, perhaps combining the functions of several F-P units in one PLC. That is a function of the I/O and logic being used on each F-P controller and the I/O available on the PLCs.
The F-P also displays data on the faceplate. This function can be handled by a touchscreen (like the EZ-Touch in the AutomationDirect.com catalog or an Allen Bradley PanelView or a GE QuickPanel). Sometimes you can network one panel to several PLCs.
If the operator wants to keep the convenience of the SCADA software on the PC you can network the PLCs to the PC and run ThinkandDo or Lookout or WonderWare on the PC and link it to the PLCs. If you have two ports on each PLC or the right protocol you can use the PC and the local touchscreens.
You should start talking to the tech support at your chosen supplier about the details. Put together a point list of all the I/O, a Process and Instrumentation Diagram showing the control loops and the equipment, and a block digram showing the control equipment and the communications link. Add a list of required features (like trending, reporting, disk access etc.) and you are ready to get your vendor involved.
If this is your first project, AutomatinDirect.com may not be the best choice. I love their products and service, but if you are "green as grass" you probably need somebody local physically there to hold your hand and help out. Some WESCO branches can do that for AutomationDirect products, but if you can't get that support locally then GE would be my first suggestion because they offer a lot of bang for the buck and generally have good support. Allen Bradley may be the next best because they also have good local support, but at a higher price and often a steeper learning curve.