What are the odds that a 2.0 amp relay output card will be able to handle the inductive load rating of aprox. 0.625A. (24VAC s.v. coil 15 watts)?
Is there a formula for converting amp ratings to inductive load?
In the manuals for that coil it should indicate the power factor, a number less than 1. Then:
Apparent current = Active current / power factor
Apparent current is what really circulates through the cable.
Active current is in your case 0.625A
Check the manual of your relay card.
My guess is that it can handle the load, but there might be a derating in the number of switching cycles that it can do before worn out.
Not sure what you mean by amp rating to inductive load.. most AC equipment load is noted in VA when the reactive load is large enough to actually matter.
With that and the power factor, you can find the resistant load and the reactive load using cos sine calculations.
it will handle the load, but not for very long. the contacts will weld together.
the surge current for that load (.625 amps) is typically 6-10 times that or 3.75 to 6.25 amps. the bigger issue is the breaking of the current, this is where the opening contacts try to arc (weld) together. even if you use a rc network in the terminals, i believe you will have issues from personal experience. would a triac output card work?
hope this helps,
james
I concur with James' observations. Solid state output modules generally have higher inrush ratings than contact output modules. But not all PLC models offer 24 VAC output modules. If yours does, a 2A, 24VAC output module would be a better choice than a contact output. If there aren't enough 24 VAC solenoids to justify a module strictly for them, consider an interposing device that would be easier to replace when it fails.
In any event you will improve your odds by installing suppression.
thanks all.
I've always used relays for this reason and others.
Only reason I asked is, this time space is an issue.
Totally remember now that the inrush current is the dealio w/ the s.v.
Triac's ring a bell.
Now to see if Wago offers triac output cards.
As James Mcquade said the problem with inductive load is the wear on the contacts when they open.
Normally 15W should be handled easily by a 2Amps relay output but it depends on the number of operation per hour so you must to be careful.
I would definitely add a varistor on the load even if you decide to use a solid state output card.
Usually solenoid valves with AC coils are provided with voltage spike suppression built in to the connector.
Like the following which has both LED and varistor built in.
https://www.mandmcontrols.com/danfo...s-power-led-plus-varistor-indicator-connector
Both AC and DC coils accumulate energy that is released on disconnection with a voltage spike that can produce a spark in the relay contacts. This is how engine spark plugs work.
As other said for me the best for AC coils is to put a varistor on the coil terminals so the spike does not flow through the cables which by induction could affect other circuits
Hi all! I nead to make acceleration ramp using s7-300 plc. Ramp must be outputed to analog output module. Time of accelerating and min/max...
3,390
Hello! Hope you are great. I need to make a change in a PLC with ladder logic. I will mount a analog valve and I need to control it in ramp up...
328
Hi hoping someone can assist me with current issue I am experiencing with an ABB drive. Problem I’m experiencing is a ABB drive supply a large...
215
I have a old lathe with a 120 VCA 9.5 AMP motor. Has white, black and red wires. I need to find a way to connect it to a variable speed controler...
103
Does anybody know how 'timestamp output' functionality internally works in a controller? I do not mean the instructions you use as a programmer...
70