analog input - diff or single ended
hapetter
Feb 2009
Kristiansand
58
Hi.
Can anyone explain the tifferent between single ended analog input and a analog differential input?
How can I choose right?
Lets say I have a 4-20mA 2 wire sensor. What should I select?
Thanks!
Best Regards
Hans Pettersson
I'm not 100 percent certain, but I believe differential cuts down on noise on your analog signal?
But if you choose differential, it uses more registers and you lose the status / config capabilities of the module.
Can anyone confirm / correct?
My understanding of single ended versus differential only applies to voltage signals.
A single ended signal means that each analog voltage input is one wire, and multiple single ended signals are referenced to one common reference voltage. So, your input card may accept 16 single ended signals, and would also have one "signal common" wire connection.
Differential signals each have two wires wo that they may each have their own common reference point. The analog input measures the voltage difference between the two points. Differential signals are less likely to have problems with noise because any noise present on one conductor in the pair is likely to be present on the other conductor as well. So the analog card will still measure the correct difference. Think of the noise as a temporary voltage offset.
Hopefully, someone with more detailed information can improve this explanation.
Paul
okie is not complete correct.
differential means it is measuring the difference between two inputs so the signal can float (not complete free as it is bounded by max voltage input. the disadvantage is it takes two input channels and more calculation.
single input is bounded to ground so not floating and.
When there is a ground loop you will run into problems.
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,143
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
259
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
119
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
88
Why AMIo800 Analog input module's I/O LED is Lighting up Red? Checked module connections, 4-20ma wires etc but this light is continuously Lighting...
112