analog input error correction
Peter North
Jul 2007
Halifax, Nova Scotia
Hello
I'm using AB compact logix with its 1769 IF-8.
For 4-20mA i configured the card to use the data format of 4000-20000.
using a simulator i force 4-20mA in each input.
for 4mA sometimes i get 3998 or even 3996,for 20mA i get 20010 to 19998.
How do i avoid out of range alarms ?
I addition,I must take into account the errors of the instrument itself.The PT100 for instance.
How do i display the correct EU-value ?
It seems to be that your simulator device is the one that is out of range, i guess your board is new, but if you trust in your devicet you can try to calibrate your board to fit into 4000 - 20000 range
Or you can try to scale your inputs so that your outputs are always in the range you want, i.e. 4000 - 20000
bill
The errors your talking about are less then .05%, thats beyond nit picking to me. There next to perfect (IMHO). The under and overrange are at 3200
and 21000, its up the the programmer to decide what to do if that occurs.
The card and processor continue to work.
To get EU from raw data is a math excerice. y=mx+b ( equation for a line)
Hey guys, I am using ML1200 with Analog module IF4. When i apply voltage (0-10V) across Terminals of Analog module i am getting wrong value on...
24
4,759
Im trying to calculate the measurement error when using a 4bit resolution input module with a 0-5V range to measure a 5V signal. What is the...
31
7,211
Hi everyone, Our company has had a problem with a vendors machine, it keeps failing parts. As we all know, no one makes bad parts so its got to...
3,315
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
30
1,159
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
270