Yes i did that but still it doesn't work properlyIf you are still "there", have you tried Input Min = -31206 and Scaled Min = -100?
This is quite interesting...
The 1761-IF4 configuration is done strictly via RSLogix 500:
either 4-20 mA or -10 VDC to +10 VDC for Input Ranges
and
either Raw Proportional or Scaled for PID Data Format.