Analog Input Fluctuations

Steve Etter said:
Question: Does anyone have a formula or rule-of-thumb for sizing filters for this type of application. I have never had to do this, so I really don't have a clue what to get.
Steve

Yes, 1/(2*PI*R*C) = Cutoff frequency. Where R*C is the time constant. The cutoff frequency should be 5 to 10 times higher than the highest frequency you want to measure. You may reduce the cutoff frequency to remove even more noise but beyond this point it is better to fix the noise problem. The equation allows you to choose R * C. Since the resistor is in series with what ever the input resisteance is, a resistor that is too big will noticeably attenuate the signal. To compensate one usually chooses a big capacitor.

A =-20 log | 1 + jwRC |
 
Mr. Jenkins beat me to it. I'd try to isolate the 0-10V signal by isoalting it through a signal conditioner, and converting it to 4-20mA.

But before I'd do that, I'd replace the 10Vdc power supply on principle. Power supplies are problematic, they're the source of many failures and the ability to swap one out in a hurry with another standard power supply is SOP in our plant. Unless there is some control reason that you're using the 10V from the drive, why not use a real power supply?

It wouldn't surprise me if replacing the supply eliminated the 'noise' factor, since it's evident that you have a grounding or more likely, common mode problem between the drive and the PLC input.

Dan
 
Since we are back to this......

I did indeed finally find the source of this problem but neglected to post it....so here is what I found.

The problem turned out to be something within the analog DC drive itself. The manufacturer, who is well aware of this issue, offers and sells an isolation board that solved the problem. Once I installed one, POOF!, no more problem.

As luck would have it, my company had previously been using one of these isolation boards on each and every application of the DC drive for years, but nobody could remember why. During one troubleshooting exercise, I decided that the isolation board was causing more trouble than it was worth, I stopped using them.

Now I know better. I only wish the guys before me had kept some records....

Steve
 

Similar Topics

I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
30
Views
1,145
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
259
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
Replies
1
Views
119
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
88
Why AMIo800 Analog input module's I/O LED is Lighting up Red? Checked module connections, 4-20ma wires etc but this light is continuously Lighting...
Replies
1
Views
112
Back
Top Bottom