L D[AR2P#0.0] Lifetime Supporting Member L Join Date Nov 2006 Location UK Posts 6,697 Apr 3, 2013 #16 I must admit when I read your first post and assumed you were getting a range of current values between 4-20mA but the PIW value did not change.
I must admit when I read your first post and assumed you were getting a range of current values between 4-20mA but the PIW value did not change.
JesperMP Lifetime Supporting Member + Moderator Join Date Feb 2003 Location ᚴᚬᛒᛅᚾᚼᚬᚠᚾ Posts 16,342 Apr 3, 2013 #17 rpop91 said: JesperMP said: I thought the values you posted earlier were the raw analog input. Click to expand... They were. I'm still seeing a bounce between 0 and -16 but that's to be expected right? Click to expand... No that cant be right. At 20 mA you should get 27648 or something close to that.
rpop91 said: JesperMP said: I thought the values you posted earlier were the raw analog input. Click to expand... They were. I'm still seeing a bounce between 0 and -16 but that's to be expected right? Click to expand... No that cant be right. At 20 mA you should get 27648 or something close to that.
rpop91 Member OP R Join Date Mar 2012 Location Detroit, Mi Posts 44 Apr 3, 2013 #18 Yes at 20mA I'm seeing 27616 and at 4mA im bouncing between 0 and -16.