Yes I have only enabled those channels for now, they both do not allow me to change the output. I’m sure it is something simple that I am missing. No my problem has not been solved. I am very puzzled by this
the electrician is going to check that switch now. i just noticed the channel shows a 1 in the overrange column. what would this indicate?
The only reason that overrange is set is because the value you are moving or copying into into module 11 channel 0 is higher than accepted, that is ( I never used PID values) in my case I always use engineering values 4000 - 20000 ( 4-20 mA) . This value is bigger than 20000.
I am testing the output from my AB 1769 L33 with a 4-20ma output card OF8C. i create a simple ladder line to MOV a value to Local:11:O.Ch0Data, but the output value doesnt change on the meter or if i connect it to an analog input. i have configured the card for 4-20ma, enabled the output and tried raw/proportional, percentage, scaled and engineering units, but the output doesnt reflect the value i give it. the output value is either 4ma or 12ma, depending on the data format, so i know it is doing something. i dont have it used anywhere else in my program. i have tried forcing it and nothing changes. please help
I don't recall whether this is the same module, but I remember encountering a clamp setting on a 1769 AO module configuration dialog and the default settings for the upper and lower clamps allowed no change to the output.
Hello! Hope you are great. I need to make a change in a PLC with ladder logic. I will mount a analog valve and I need to control it in ramp up...
319
I have a 170AAO92100 card that I am interested in using as a 10 volt output. Is there setup that I have to do in order to change output or simply...
86
Hi We're having issues with an FX1N-1DA-BD Analog output module. We're using an metallic contamination sensor MCS 1000 to detect particles. This...
109
249
I have a program that I am gradually piecing together (my first program). There are 4 cascading timers that turn Y001 and Y001 + Y002 on and off...
544