Analog output variations

erivinoth

Member
Join Date
Jun 2011
Location
pondy
Posts
29
Hi,

One of our project using SLC5/05 processor and 1746-NO4I 4-channel analog output module. 4-20ma current output used. When we put 0% (From HMI)we are getting 3ma and when we put 100% we are getting 14ma only we are not getting 4 & 20 ma in 0% & 100%. Output impedance is 250Ohms This output is connected to Quarter turn Modulating actuator. Can anyone give me the solution for this issue.

Thanks,

Regards,
Vinothkumar
 
Show us a screen shot of how you are scaling your 0 to 100% for the output in your PLC program, or better yet, zip and post your program.

Have you checked your PLC power supply load? You can check that in RSLogix500 under IO configuration. Click the power supply button and select the correct power supply. Loigx500 will indicate if you have a large enough power supply for the configured IO.

Have you checked the switch on the Analog Output card that selects internal or external power?

What happens if you disconnect the wiring and attach a 250 ohm resistor?

Lets start first with the program though, since scaling is a common error.
 
Last edited:
Hi,

Thanks for your reply, Actually this is existing system which is installed 10 years before. Worked well. This PLC is Password protect so i could not see the program. Totally there are 8 actuators, all are same function. other actuators are working fine. They are used internal power supply.
 

Similar Topics

Hello! Hope you are great. I need to make a change in a PLC with ladder logic. I will mount a analog valve and I need to control it in ramp up...
Replies
7
Views
329
I have a 170AAO92100 card that I am interested in using as a 10 volt output. Is there setup that I have to do in order to change output or simply...
Replies
0
Views
90
Hi We're having issues with an FX1N-1DA-BD Analog output module. We're using an metallic contamination sensor MCS 1000 to detect particles. This...
Replies
1
Views
114
I am having trouble with getting no control of my analog output signal. I am using the SCL function block to control my analog output. The logic...
Replies
11
Views
257
I have a program that I am gradually piecing together (my first program). There are 4 cascading timers that turn Y001 and Y001 + Y002 on and off...
Replies
8
Views
549
Back
Top Bottom