Analog Output
TOMC
Apr 2002
Niagara Falls
58
Its a long weeked here in Canada and I have been working all of it.
Aside form lack of sleep my problem is this.
I have a Modicon DAU 204 analog output module that is set for 0-10vdc output. It is to be conected to an SMC ITV3000 proportional regulator. The SMC regulator is wired so that the 24vdc supply power and the 0-10vdc analog input share the same 0vdc common.Somthing about this just does't seem right or am I just to tired. :eek:
This is probably OK. Draw a loop diagram, showing the power and signal connections to the anaolg output card, the power connection to the regulator, and the signal connection to the regulator. Now follow the current path around all of these circuits. If you only have one common point for all connections your circuit is alright. If you are connected at more than one point you may need isolation.
After reviewing the Modicon DAU204 module wiring, I can not see any problem with combining the regulator and module 0V terminals.
Hello! Hope you are great. I need to make a change in a PLC with ladder logic. I will mount a analog valve and I need to control it in ramp up...
320
I have a 170AAO92100 card that I am interested in using as a 10 volt output. Is there setup that I have to do in order to change output or simply...
86
Hi We're having issues with an FX1N-1DA-BD Analog output module. We're using an metallic contamination sensor MCS 1000 to detect particles. This...
109
251
I have a program that I am gradually piecing together (my first program). There are 4 cascading timers that turn Y001 and Y001 + Y002 on and off...
545