I am doing "module analog 1769-OF2 PLC rockwell" four types of data "Engineering Units ; Scaled-for-PID ;Percent; raw/Proportional data " data each type used when . differences between the four types .you can send through email ([email protected]) .Thanks
when to use each type
Raw/Proportional Data:
Gives you a wider range for slightly better resolution.
Engineering Units:
Represents the electrical output range.
0-10v ( 0-10000 raw data) 4-20ma ( 4000 to 20000 raw data)
Kind of a build-in meter.
Scaled-for-PID:
Use when using a "PID" instruction. The "PID" instruction will output 0-16383
raw data for it's "CV" No need to rescale it for the output card.
Percent Range:
When you the programmer like to see the output represented by a percentage value.
maybe you could explain what you trying to do with the analog signal ie: just read the value or control an output to a valve ect...
I think Mickey gave you a pretty good answer, and I don't think you are going to get a better answer at this point. It depends on the situation and the design goal. We can't really give you a specific answer without a specific question. If you have a specific question or situation, then post it.
Stu....
Hello I need to message read the entire 16 channel raw analog inputs from a 1769-L33ER Compact Logic controller to another 1769-L33ER Compact...
254
Hi all, I’m an electrician with limited knowledge of PLC circuits. Typically I will see simple 2/3/4 wire terminations for transmitters on...
26
1,289
Hi all, I want to catch min piks of an analog signal when digital signal is on(pls see the attached oscillogram). My hardware is 5069-L306ER CPU...
1,010
Hello, the PLC in question is 1769-L30ER. I have a local 4-20mA Analog Output module (1769-OF4CI), and also a remote ethernet PointIO analog...
408
I need to change my program to increase a IP transducer by 0.5 psi every 5 seconds. I am making a automated pressure tester using a pump, IP...
1,063