Anybody know how many PV's a SLC 5/04 can support?

ssjauto3360

Member
Join Date
Feb 2021
Location
indiana
Posts
3
I was curious as to how and how many panelviews i could connect to one SLC. I have a 1747-L542 B processor. Any guidance would be appreciated. Thanks.
 
Last edited:
Thanks for the reply. No, not trying for anything extreme. I am just new to AB, and I have the aforementioned SLC and a panelview 900, and i wanted to have another panelview at another location and I wasn't sure if it was possible or how to go about it. The SLC and the PV 900 are just going to be hardwire connected via data highway cable and i didn't know (if it was possible to have more than one) if i could just double land the wires at the SLC or how to go about it.
 
Most DH+ installations are very straightforward: two wires and a shield, in parallel, daisy-chain fashion.

One termination resistor between the blue and clear conductors at each physical end of the network. 150 ohm for 57.6 kb/s or 115.2 kb/s, or 82 ohm for 230.4 kb/s. Two termination resistors total, no more, no less.

Two PanelViews and one SLC-5/04 will be no problem.
 

Similar Topics

I am trying to connect with a Schneider plc which has a firmware version only available in Somachine v4.2. In Machine expert After taking upload...
Replies
0
Views
113
Hi All, At work we primarily use Rockwell products and they are pretty good to work with and rock solid for industrial environments. A little...
Replies
3
Views
1,066
11 months ago I ordered a 10" Redlion HMI. I was given an April delivery date. April came and went. I waited, and in June I asked our vendor...
Replies
7
Views
2,373
If I want to think about PLCs, I come here. For Home Automation there are various good forums. When Mum was alive, I had two or three...
Replies
11
Views
5,118
Back
Top Bottom