AS-I Network Cable Question

Well how would one know wich cable your customer might have in use?

But in general, any high power 2x1.5mm2 (dunno the awg size, awg sizes are ******** anyway) should suffice. One reference says H05VV-F 2x1.5.
 
Terminators on ASi network

Hi All

If i fix two terminators on ASi network on length less than 100m, will it cause any other problem

Because we are not sure of network length inside the cable trays (many surplus cables)

Thanks in Advance
 
There is asi terminators also. If there is no problem with said network, why add any? If there is problem, first add one on other end, then if it is not enough add second. If those wont do the trick, you can try tuner (active terminator).
 