Atex Zone 1 PLC
kimao
Aug 2012
Vestcoast
Hello
Do any of you know of a PLC with an Atex Zone 1 approval? Does this exist? We have an application on a piece of mobile equipment where we need the PLC to be in the zone. Enclosing the PLC in an ExD cabinet is not an option.
Thank you
From what I have seen on the web the best you are going to find is Zone 2 stuff. I would say you have 2 choices: 1) Move the PLC out of the area or 2) Put it into a Purged Box.
I agree with Bullzi 100%.
Siemens and Stahl have HMI's for zone 2 but not PLC's.
Siemens can do conformally coated PLCs, which I think have the lowest possible zone 2 rating. Maybe, with lots of limitations and a big price tag attached.
Your best bet is to build the PLC and hardware in a purged cabinet. A bomb (explosion) proof cabinet might be an option, but would be a right pain to build.
If the customer does not want purged or bomb proof cabinets then your only option is to fill the enclosure with epoxy and turn it into a giant brick.
You wouldn't be able to use circuit breakers, because you have just glued it on, and all relays would need to be sealed or they wont work (glued on or off).
If one of the fuses pops your screwed because its near impossible to dig it out of the epoxy. Your pressure transducer wiring can't be replaced for the same reason.
Purged cabinets are the future for you :)
What you refer to as a bomb proof cabinet is an ExD enclosure. This might be a problem due to it's size. I see some vendors have HMI's or IPC for Zone 1. Putting a soft PLC in one of these might be the solution. I/O in Zone 1 is not a problem.
Hi - I am searching for an M12 panel receptacles to use for ethernet connections. I see lots of M12 cables that are ATEX / C1D2 rated but nothing...
1,011
Hi, Can someone with experience help me with the ATEX directive. We need to put the control cabinet in the zone 21 and it is certified for this...
2,792
Hi All, In know this topic is not an actual PLC-problem, but i hope you guys can help me anyway. I have a motor placed in the ATEX zone 1 area...
2,824
Who makes an HMI touch screen that has ATEX certification for Zone 2? AB does not. Stahl makes one, but if it has the same software as 5 years...
8,023
Hi, I have an application which is in an ATEX hazardous area, the instrument being used is lower power and qualifies as 'simple apparatus' and...
2,363