Hello everyone. I've been away for quite awhile... My questions is more logic based than PLC programming per say.
I'm using a Do-more processor with C-more HMI. I have PID to time proportional control to dc Watlow Din-a-mite SCR contactors. I've used this set up many times for platen heat control on rubber presses. I bypass the PID with heat at 100% until I reach 90% of set point then PID takes over cycling heat to reach / hold the set point.
We are controlling 4 x 12KW heat boxes located on a 40' x 5' autoclave. A blower circulates the internal air 100% of the time heat is on.
Problem is we have burnt up multiple heat elements. All wiring and voltages have been triple checked and verified. The TC have been certified to our display in the HMI. Some are saying we need to cycle the heat elements so they can't sit at 100% for "too long". I have never (10years +) had to program this into any heat control. We have no criteria on what is "too long". We have no way to check the heat (currently) directly at the element. Heat is currently checked via 2 type J TC. The theory was the heat would be relatively close throughout the chamber via the constantly circulated air.
FYI it takes about 2 hours for the heat to go from room to 300F. From there the heat would reach / hold set point via PID.
How could the elements get "too hot" with a set point of 330F and a chamber temp reading of <300F? Specifically has anyone done any large autoclave specific programming / heat control? Everyone is pointing fingers now... I greatly appreciate any educated suggestions.
I'm using a Do-more processor with C-more HMI. I have PID to time proportional control to dc Watlow Din-a-mite SCR contactors. I've used this set up many times for platen heat control on rubber presses. I bypass the PID with heat at 100% until I reach 90% of set point then PID takes over cycling heat to reach / hold the set point.
We are controlling 4 x 12KW heat boxes located on a 40' x 5' autoclave. A blower circulates the internal air 100% of the time heat is on.
Problem is we have burnt up multiple heat elements. All wiring and voltages have been triple checked and verified. The TC have been certified to our display in the HMI. Some are saying we need to cycle the heat elements so they can't sit at 100% for "too long". I have never (10years +) had to program this into any heat control. We have no criteria on what is "too long". We have no way to check the heat (currently) directly at the element. Heat is currently checked via 2 type J TC. The theory was the heat would be relatively close throughout the chamber via the constantly circulated air.
FYI it takes about 2 hours for the heat to go from room to 300F. From there the heat would reach / hold set point via PID.
How could the elements get "too hot" with a set point of 330F and a chamber temp reading of <300F? Specifically has anyone done any large autoclave specific programming / heat control? Everyone is pointing fingers now... I greatly appreciate any educated suggestions.