Automation Direct V Memory (RAM EE memory)
Thank you very very much, Mr. Vaughn, Mr. Bernie and Mr. Mark. Your help tough me a new chapter. Especially Mark brought me to the new world that full of knowledgeable and generous experts. Mr. Mark, Thanks again for your honesty.
I studied and tried the rung. It seems working. My next question will be: 1) How am I sure the data is in the EEPROM V7401, for example, not in the retentive V7401 RAM? 2) The book suggests for one scan. If I use C0 in the C-more, as you posted, would that cause too many writes during that touch of C0?
Gordon
Actually, after the 'store' rung executes the data will be in both places. The acting program uses the information in the RAM area. Only on startup is the EEPROM copy transferred to the RAM area. So if, for your own curiosity, you wish to check this once then note the status of the RAM area, 'store' it then change one of the RAM areas. Don't perform the 'store'. Cycle power and see if the RAM is restored to the previous contents. There is no way during run time to directly test the EEPROM contents.
And you are correct. My example should have used a differential contact of C0, not the standard contact, to ensure that the MOV command is executed only once, not many times during the holding of the HMI button.
I have a Direct Logic DL05 (DO-05DR) PLC I'm using with a samkoon touchscreen. I've got communication going between the two using Modbus, but...
25
7,544
Hello, I have an automation direct d2 262 plc and C-more HMI EA9T6CL-R. I need to prepare a program, scheduled to be performed on a future date. I...
161
Hello all- I have a unique challenge using a customers Direct logic 06 PLC. This customer has a DC motor operating at 10 RPM which is turning a...
161
Hi, I have been trying to run drive via Sysmac studio. I can ping the drive. I can see the logic bits going on/off as per command. But, drive is...
21
642
Anyone tried Automation Directs new CM5 HMI. We've been the EA9's for a few years now with minimal complaints. A few failures here and there but...
17
1,700