Bit Level Addressing
schuma01
May 2019
Minnesota
I am currently using Micrologix 1100 connected to my pc using RSLinx Lite. I need to file data from Keyence IL series lasers using DL-EP1 module. I have communication and have put together my ladder but keep on getting the error, Address mus be specified to the Bit level. I am sure everyone has heard this before but I am not sure how to proceed. Any suggestions?
Can you take a screen capture of error and the line that it is complaining about?
That may mean that you have used XIC with a word specification instead of a bit specification.
Example:
I:0 O:0/0
The XIC is specifing world 0 of inputs. The correct convention is:
I:0/0 O:0/0
Inputs word 0/bit0 (or whatever word/bit is correct for you).
To expand on what g.mc stated above..
I haven't used those lasers, but the other Keyence products I've used only transfer data in words.
If that's true, then let's say you're receiving a word N10:0, which has a fault status in bit 0 and producing status in bit 1. You would have to address the fault status in the logic as N10:0/0 and the producing status as N10:0/1.
If you try to do a XIC or XIO instruction with the entire word N10:0 you'll get the error you described.
Hello everyone... I need to enable a float value(Analog output) through a bit input. Kindly help me to do the same
1,466
Can a %R Register (or any other word type) data be addressed at bit level? ex. Register = %R0001 Can I use it in ladder where I am looking at...
3,535
I have a PLC5 program that I converted to Logix5000 platform with the automated translation tool. Everything went fine with that, but my problem...
3,237
I am using the latest version of Crimson 3.0 connected to a Allen Bradley ML1400 and can not seem to address a B3 word to the bit level. I have...
3,839
Hello, Haven't been on in a while. I need to generate a bit level pdf of the I/O for RSLogix 500. I can generate a report but it just shows the...
163