thanks Mike

I've heard tell of overloads 'getting weak' but never had independant verification that the alloy was the cause. Very intersting, never know what tidbits you can pick up here.
One softstart starting several fans......hmmmm.....that I have to ponder.....
 
Not Rocket Science

You can calculate the acceleration time fairly simply. The formula below assumes across the line. If you are using a RVSS you can set the acceleration torque. Remember, if this is a belt driven or gearbox driven fan the inertia at the motor shaft is proportional to the square of the speed ratio.

accell.jpg
 
Tom, the problem is that you don't know the torque. You know the starting torque because it is the line-start torque reduced by the square of the starting voltage reduction. But, as soon as the motor starts to turn, two things happen to make the torque difficult to predict.

First, you have the usual NEMA B torque speed curve which, at any constant voltage including reduced voltage, is far from linear, much less horizontally flat!

Second, the softstart is ramping up the voltage as the speed increases so, on top of the above, you have the voltage steadily moving back to full line voltage. That puts a decidedly upward slope on the already non-linear torque curve and, if that isn't bad enough, you don't know just where in the torque-speed curve the voltage reaches full line level since the voltage ramp is based on time. I've seen the time set so short that full voltage occurs before the speed reaches break-down torque level and I've seen time set so long that full voltage isn't reached until several seconds after the motor hooks up in near-synch mode and is running near normal speed (lightly loaded).

All of that makes accel time on a softstarter nearly impossible to calculate and high risk to predict! Field trial is the only reliable way I've found to determine accel time and, even then, you are never sure the test load torque matches true running conditions.

Softstarters are nice but precise they are not! For precise you need an inverter with an enforced accel ramp.
 
Well, Dick, I'm going to bow to your superior experience.

I've used the above formula successfully to determine acceleration times for across the line starts. I guess I was mislead by the torque ramp settings on the RVSS, and "assumed" (I'm old enough to know better, too) that it would give a linear torque increase with a useable average torque. To tell the truth, in the field I've always just kicked up the acceleration time until I could get the motor started, and never done any analysis on it.
 

Similar Topics

I have an application on which I would like a few comments/ideas etc. I am not looking for specific programming here, just a concept analysis...
Replies
34
Views
16,183
Hi, I need some help to find out the reason for the blower motor tripping . On one of our machines we have three 10hp 575v blower motors. These...
Replies
26
Views
14,343
I have not receive my plc tutorial yet (ccnow order number 13-3860) and I am quite new to PLC..so I have two pressing question for our panel of...
Replies
4
Views
6,075
Customer want to use contactor for their 5HP motor blower application. im leaning to VFD. anyone use contractor for blower application...
Replies
9
Views
212
I've got 6 identical regenerative vacuum blowers powered by 6 identical drives in 3 identical panels all fed from the same 1 main building feed...
Replies
27
Views
888
Back
Top Bottom