One of many possible explanations.
Does the blower in question get up to speed ?
If there isn't enough torque to accellerate the impeller, the speed may rest in some intermediate level.
If you plot the blower load/speed curve and motor torque/speed curve in the same diagram, there might be a weak spot where the two curves touches or almost touches each other. Pumps and blowers have exponential load curves that run almost parrallel with the emotor torque curves in the starting range. Thats why they can be so hard to start up.
Then why does one blower start and the other not ?
Because there are always small differences in the manufacturing of both emotor and blower. That, or the blower is running backwards as previously suggested.
Does the emotors have thermistor or Pt100 sensors in the windings ? If they have, you can install overload protection based on these, and then crank up the overload relays to a much higher value. This will either allow the blower to start up, or allow you to check the speed with a speed tester before the blower really trips.
If there is some kind of throttling element (aka damper) in front of the blower, check that this is working properly. It should be closed or almost closed to ease the startup of the blower.
Does the blower in question get up to speed ?
If there isn't enough torque to accellerate the impeller, the speed may rest in some intermediate level.
If you plot the blower load/speed curve and motor torque/speed curve in the same diagram, there might be a weak spot where the two curves touches or almost touches each other. Pumps and blowers have exponential load curves that run almost parrallel with the emotor torque curves in the starting range. Thats why they can be so hard to start up.
Then why does one blower start and the other not ?
Because there are always small differences in the manufacturing of both emotor and blower. That, or the blower is running backwards as previously suggested.
Does the emotors have thermistor or Pt100 sensors in the windings ? If they have, you can install overload protection based on these, and then crank up the overload relays to a much higher value. This will either allow the blower to start up, or allow you to check the speed with a speed tester before the blower really trips.
If there is some kind of throttling element (aka damper) in front of the blower, check that this is working properly. It should be closed or almost closed to ease the startup of the blower.