Brabender DL-4000 to SLC 5/05

B Fix

Member
Join Date
Nov 2008
Location
ND
Posts
17
All,

I have a customer that wants me to message between a SLC 5/05 processor and a Brabender Congrav RC4 using a DL-4000.

Do I use the SLC cable that is used to connect my PC to the SLC channel 0 to connect the DL-4000 to the SLC 5/05, or do I have to use a different cable?

I was sure cause I know that for my computer to see the SLC on channel 0, I need the special cable and I can't just use a normal one, so I was just wondering if I still need to use that special cable for the SLC to DL-4000 connection.

Thanks!
 
All,



Do I use the SLC cable that is used to connect my PC to the SLC channel 0 to connect the DL-4000 to the SLC 5/05, or do I have to use a different cable?

Thanks!

Yes, nothing special just a null-modem cable.

nullmodem.jpg
 

Similar Topics

I have 16 cb_E connected to OP16 via fiedbus and the cb-E connected to l60 controllogix via en2t ethernet. using generic module in IO config so I...
Replies
2
Views
1,734
Hi All, I'm setting up a Brabender feeder via Ethernet I/p, I have the start and stop figured out but the int to real has me up against the wall...
Replies
2
Views
2,820
Hello Friends We have 10 Powerfocus 4000 with DeviceNet, We need to backup the configuration, the Powerfocus is detected but as unrecognized...
Replies
0
Views
108
Hi, as part of a project to bring an old retired power plant back on-line we need to access a single existing TT4000 HMI used to interface 2 Solar...
Replies
0
Views
459
who can teach me how to edit tag adam 4017+ in citect scada? real external I/O
Replies
0
Views
880
Back
Top Bottom