Calibration of pt100
No. O deg C = 100 ohms hence why it is called a PT100 so ambient means nothing
[FONT=&quot]You only compensate with thermocouples. Primary measurement elements that generate a milli-volt signal. PT100 changes in resistance as temperature changes.
100 [/FONT][FONT=&quot]Ω[/FONT][FONT=&quot] at 0°C and then add 0.39[/FONT][FONT=&quot] Ω[/FONT][FONT=&quot]/°C [/FONT]
Yes when the equipment is to be calibrated and not the sensor.
No when you want to calibrate a sensor only. (However this is depending on more factors like pressure, medium . Most people use a small heatfurnace with a referencesensor.
I only use ICE water to get them to Zero according to USDA req.
When calibrating pt 100 do you also compensate for ro temperature and why?