We have a Hengstler A58 Can Open Encoder connected to a CM Can Open Interface card for Siemens S7-1200 plc.


{Encode}|BusTerm|============= { PLC}

When we have above connected with 3m Cable the Encoder and PLC interface work ( we have a solid green power light and get data)

When we have above connected with a 10m Cable the Encoder doesn't work ( we have a green power light and a red flahing error Light) .

Both the 3m & 10m Cables are wired the same and are provided by the Encoder Manufacturer with a moulded Plug on one End. If we swap back to the 3m it will work ?


Inside the Panel is a 18.5KW VSD (Siemens GC120C) and a PLC (S7-1212C DC/DC/DC) and some MCB's .


Only thing to notice was that when the VSD is running my Laptop (connected over ethernet locally to the PLC would loose its internal mouse guessing though EMC noise.

Reading the data on CanBus it would appear to be immune to nois so i'm at a lost on whet to do next..

We need the 10m Cable we can't live with the 3m one.....
 

Similar Topics

Hello. I need to connect an EtherNet/IP adapter to CODESYS RTE. I have confirmed that the adapter works with Rockwell Logix, and not only the...
Replies
7
Views
2,443
Hey everyone, I am seeking assistance on finding and solving potential cause of a Modbus RTU issue, from a Micro820 PLC. We are unable to...
Replies
6
Views
1,317
Hey Guys, I am struggling to read data from a "JUMO" make controller using modbus RTU with MLX1400. The communication between the devices has...
Replies
18
Views
5,090
I have had to write my own Modbus ASCII "driver" for an old DL05 talking to a GS4. I am using the Modbus Slave program for testing. A PID is...
Replies
17
Views
7,011
Hi All, I have a question would like to ask the experts: my system has two Rx7i PLCs and I'm having them communicate with an RTU (D25) via modbus...
Replies
2
Views
2,073
Back
Top Bottom