Can I get data via USB thru a Siemens TS Adapter-II module?
dmcswain
Sep 2006
York, SC
Hi folks - I'm setting up a central data historian at a customer's plant. I need to get data out of an S7-300 but the only port free on the rack is the USB on a TS Adapter II module.
The TSA-II manual says, "The TS Adapter II allows data exchange between the programming device or PC and an S7 system via the Universal Serial Bus (USB)." So it sounds like it can do what I need, but I haven't found an OPC supplier who knows how to support this connection.
The PLC is maintained by a 3rd party and I'd rather not open a can of worms by requesting hardware changes, plus I'm trying to keep costs down for the customer. So any suggestions on making the USB work would be greatly appreciated!
So you need an OPC connection to an S7-300 (which type no exactly) ?
I am not 100% sure but I think Kepware's OPC server for the serial PC adapter will also work with the TS Adapter II via the serial port. You can download a demo from Kepware site and try it out.
I've used this adapter for step7 programming through usb
I would say through Siemens SimaticNet opc this should work fine. The selection should be in the pg\pc interface once the teleservice software is installed
Look at the SimaticNet manual and make this is supported
I'm going to look at the manual too
What processor is this??
Just because there are connectors on the ports doesnt mean you cant put a CP (ie 5611) in your PC and still
connect to the S7 cpu
JRW, are you saying that the Teleservice adapter can be inserted in a "PC Station". That is the requirement for setting up the OPC server with Simatic Net.
The regular PC adapter cannot be inserted in a "PC Station".
Hi!
Maybe Softing has something for you? The TS Adapter isn't specifically mentioned, but it could still be worth a call. Link.
I coldn't make the link directly to the page working, but select
Industrial Automation/Product/Technology/OPC/Industrial Level Communication/S5_S7_OPC Server.
Kalle
Dear All Now we use controllogix5000 as controller and panelview plus1000 for Display all required parameters as work site that more than 100...
1,637
Hello, Thanks in advance. How can I send more than 82 characters using AWA or AWT? to Zepra Printer via serial Rs232 communication? Normally I...
768
Hello, I have a project where I need to use a CLX to communicate with a 3rd party device that exchanges data via XML formatted commands and HTTP...
1,716
Hello friends We communicate between Micro 830 and a card that control DC motor via modbus RTU. We do not have any problems in communication. But...
1,525
Hi All, I need a step-by-step method to insert and update lines in the database SQL Server via software builded in FT View SE. Thanks. Fabricio
60
18,779