Caution when clearing GE 90-30 I/O fault tables?
timothy585
Supporting Member
Apr 2021
Cajun Country
47
I'm online with a 90-30 using PAC ME 9.8
No one has gotten online with this PLC for many years and the the I/O fault table has a total of 1209 faults. 1177 are overflowed and 32 are actually displayed...and these date back to 2001.
There are about 140 Genius I/O module located throughout the facility and about 75% of of them have blinking "UNIT OK" LEDs. This indicates a fault of some kind on an I/O point on that module.
Every alarm currently in the fault table is a Code:2 Diagnostic Alarm.
I don't seem to have the ability using the software to clear individual faults. It seems the only option I have is to clear the entire fault table. My question is would this be safe to do and not cause I/O to change state while the processor is in RUN mode? I can't take the processor out of RUN mode right now as that would bring the entire facility down.
Short versions - does clearing fault table affect I/O state or take PLC out of RUN mode?
Thanks.
I concur. Clearing the PLC's fault tables will not take it out of run.
However, I don't believe clearing the PLC fault tables will clear the faults on the Genius modules. To clear those faults on the individual Genius blocks, you will need to use the Genius handheld or else write logic to send a datagram to each block. That's based on my (72 year old) memory, not on reading the manual.
I know I've cleared the genius module faults on rx3i series without the handheld for sure.
I think I remember doing it with PME9.0 on the later gen 90-30's but I can't say for 100% certainty.
CAUTION: This will be a long post. I get a little confuse with MOVD (MOVE Digit) instruction of omron PLC. According to an explanation I...
2,753
Hi Guys, Where can I find more details about this yellow triangle in the program ? Why is this showing up ? Thanks
17
5,543
What Does the Caution symbol that is located on the lower right hand corner of the File Folder icon mean? I'm a total newbie when it comes to...
2,188
Good day all. I have a dip-tank that contains acid and this tank is heated by a 12000watt heater. The way the control was wired was: when SP is...
18
7,247
10 [FONT=arial]a[/FONT For As we have in our skin pass mill using Magna scale for position feedback The Magnascale sensor is assemble in each...
8,349