Can anybody explain channel level diagnostic features in DI/DO and AI/AO cards. Is there any special circuitry or hardware which is different from normal cards
What cards? What features?
Safety class digital inputs generally monitor to make sure that the proper Tx pulse train is received at the input.
Digital outputs can have electronic trips to shut down a channel on output overload. They can also have open circuit detection, generally by putting a low potential or pulsed current out to see if there is an actual load.
Analog inputs like 4-20mA inputs have a live zero detection, and out of range detection.
Analog outputs can also use a low-potential or pulsed waveform to determine if there is an actual load present, and can monitor for overload conditions.
Thermocouple/RTD inputs can tell if there is an open circuit, or short for RTD's.
Encoder input modules, depending on configuration can detect open channels by not seeing a complementary pulse on the opposite channel, or on the NOT channel for differntial inputs.
Good morning! I'm trying to find a DIN rail-mountable 4-0channel PWM amplifier that is capable of accepting a 5VDC PWM with a maximum frequency...
109
Problem: Our PLC can only output 4-20mA, but the actuators it needs to control, modulate based on a 0-135Ohm signal. Buying 4 or 8 individual...
277
Hi, Had a discussion with a cunsultant about safety and he claimed that for example an Allen Bradley MC1 (two contacts) magnetical non-contact...
1,003
Good day. I encountered a problem when calibrating a channel on the IF16H module. The module is located in the local backplane along with the...
745
After I tried wiring, I used computer program communication to read the PLC N value, but received a NAK signal. And the DL3500 CHA light keeps...
430