Citect 7.2

hazey

Member
Join Date
May 2003
Location
Australia
Posts
73
Hey guys I have a problem with a new installation with a Citect machine.

The Citect 7.2 machine is a new setup and is connected to a Controllogix ver19. A page has been made with a few tags on it, all good so far. The page reads the tags OK, but I cannot get the Citect to write to the tags. The Kernal is showing no attempted writes. Plenty of good reads coming through. I have tried a DINT tag and a Digital but neither will change state in PLC.

Using ABCLX driver.

There is another server connected to the same PLC, a Citect ver 6.1. This machine writes and reads OK, no problems. I added the same tag briefly to the 6.1 version and it works fine. I then deleted tag so it was not in both servers.

Does the 7.2 version have a read only state??

thanks

hazey
 
Hazey

Make sure that you are logged on, Citect won’t write to a tag if you’re not logged on.
If it is this then this feature can be disabled using a Paramater.
Section name: LAN
Name:Sercurelogin
Value:1

Chris
 

Similar Topics

Hello, the system we use is Scada 7.5 series. We have usb key activ now we need additional key to make the system work, how do we solve this...
Replies
0
Views
50
So i've been at this for a long while, i have Citect Scada 2018, i have full access to everything but i can't seem to find any option or...
Replies
0
Views
70
Hello, i've been at this for months now, i tried creating accounts on the aveva website but it seems to never approve my accounts or at least when...
Replies
3
Views
100
Hello, I have a running project on Citect v5.42 and simatic net v6.4 I have created a new spare PC and loaded all software like Citect, station...
Replies
0
Views
78
Hello everyone, In a factory where we installed Citect 7.20 the computer began to show the first signs of end of life. They never considered...
Replies
0
Views
84
Back
Top Bottom