Hey guys I have a problem with a new installation with a Citect machine.
The Citect 7.2 machine is a new setup and is connected to a Controllogix ver19. A page has been made with a few tags on it, all good so far. The page reads the tags OK, but I cannot get the Citect to write to the tags. The Kernal is showing no attempted writes. Plenty of good reads coming through. I have tried a DINT tag and a Digital but neither will change state in PLC.
Using ABCLX driver.
There is another server connected to the same PLC, a Citect ver 6.1. This machine writes and reads OK, no problems. I added the same tag briefly to the 6.1 version and it works fine. I then deleted tag so it was not in both servers.
Does the 7.2 version have a read only state??
thanks
hazey
The Citect 7.2 machine is a new setup and is connected to a Controllogix ver19. A page has been made with a few tags on it, all good so far. The page reads the tags OK, but I cannot get the Citect to write to the tags. The Kernal is showing no attempted writes. Plenty of good reads coming through. I have tried a DINT tag and a Digital but neither will change state in PLC.